Default Air won't cool Model 5291

I have a Gulfstream Yellowstone 5291 with 3 slides, I have had several problems with factory quality, but my problem is the air won't cool the unit if all slides are out and it's over 82 out the best I can get at counter height is 79 inside. With slides in it does better. Has anyone had this problem and do you know of a fix or is your same model working.
Glen
Glen is offline   Reply With Quote
Old 08-19-2008, 08:33 PM   #2
RCSMITH
New Member
 
Join Date: Apr 2008
Location: Souderton, PA
Posts: 7
Default ac

If the ac unit runs continuously, the coils may frost over. Set the thermostat high enough that the compressor cycles on and off and gradually drop the temp. If you set thermo. low the compressor
runs non stop & frost can build up blocking airflow. If the unit cycles, frost has a chance to melt off.

RC
__________________
Rich
RCSMITH is offline   Reply With Quote
Old 08-20-2008, 08:43 PM   #3
Glen
Junior Member
 
Join Date: Aug 2008
Posts: 6
Default Still no fix

Got motor home back today from RV service shop and Gulfstreams dealer claims air conditioner is doing all it can. It even cools unit a little if you leave the dining room slide in and close all curtains and shades. I guess there answer must be to keep this slide closed and caulk around it or only camp on cool days or stay out of Florida.
Glen
Glen is offline   Reply With Quote
Old 08-23-2008, 08:43 PM   #4
mfa
Senior Member
 
Join Date: Sep 2006
Posts: 305
Default

Does your MH have the 15,000 BTU AC or the 13,500 BTU AC? In my experience, the 13,500 BTU unit is going to struggle to cool a MH your size.

One thing that can help -- the thick insulated vent cushions you can find at Camping World. A lot of heat & solar loading comes in through the vent areas. We use these cushions in two of our vents in the summer.
mfa is offline   Reply With Quote
Old 08-23-2008, 09:45 PM   #5
Texas TC
Senior Member
 
Join Date: Apr 2007
Posts: 444
Default

We have a 13500 btu unit in the front of our 34' SuperNova and a 11000 btu unit in the rear. We go to Florida in the summer a lot to visit the kids and grand kids. I had limo tint added to the bedroom windows and wife made covers to go over the windows in the living area. These additions have worked well to keep our coach frosty cold all summer in Florida and in Texas.



__________________
2008 SuperNova (6331)
2011 Jeep Wrangler (Toad)
Now: 2011 Winnebago Journey Express
2011 Silverado 4x4 Texas Edition Extended Cab (Toad)
Texas TC is offline   Reply With Quote
Old 08-24-2008, 12:21 AM   #6
RJ82much
Senior Member
 
Join Date: May 2005
Posts: 572
Default

Glen,

There is another cause for lack of cooling that keeps popping it's ugly head. There have been many cases where the factory failed to remove tape (or cut coverings? ) from the air conditionor's chamber into the ceiling ductwork. It sounds almost impossible to believe, but it has happened more than a few times. This assumes your unit has ceiling ducting like the class A's. If so, the easy fix is to cut the openings into the duct. Somehow, the factory seems to forget this minor detail (sarcasm showing)

Anyway, do you feel cold air at all? Do you have a ceiling vent system? Is there a lot of air movement if you open the AC vent directly into the room?

Also, if the interior of our coach is really warm, I run the ceiling exhaust fan for a while to remove the hottest air. From there, the AC unit can comfortably take over.

Something is drastically wrong if the best your air can do is 3 degrees of cooling.

Let us know what you find after an inspection.
__________________
Bob

'05 Sun Voyager #8351
https://www.much2see.com/index.html
RJ82much is offline   Reply With Quote
Old 08-30-2008, 04:11 PM   #7
Glen
Junior Member
 
Join Date: Aug 2008
Posts: 6
Default still hot and so is air!

Still hot after days of phone calls and e-mails. Duo Therm claims it's not their fault, it is Gulfstream for wrong duct size or undersize unit. Gulfstream says unit is fine and I am the only one with this problem. Dealers say all their units like mine cool great, even the one with the large window in the front. Either someone is not being truthful or with this and the other 50 or 60 problems I've had maybe it's time for us all to admit, I got a lemon. This unit was bought new in March and spent half its life or more sense with them or me working on it! We have gulfstream warranty, Duo-Therm warrenty, and we bought the 7 year warranty on top of that. All the warranty plans will be pretty safe since unit is to hot to use in hot weather and none are willing to fix at this point?
Glen
Glen is offline   Reply With Quote
Old 08-30-2008, 09:55 PM   #8
RJ82much
Senior Member
 
Join Date: May 2005
Posts: 572
Default

Glen,

I understand that you are very frustrated, and rightly so. I'm very disappointed with your dealer. That said, there are some things you need to do and need to explain to us.

Does your AC unit blow cool air? If you open the discharge vent directly into the room, does cool air blow down into the room? Do you have any kind of a thermometer that you can hold in the airstream right below the AC to determine the temperature? Is any air blowing?

If there is air blowing, and it is cool, then you are going to have to remove the grill & foam filter. With a flashlight, look into the discharge chamber & see if you can find an opening in the box on both sides where the airflow can flow into the roof duct system. If there are no openings, then there is a problem.

So, if there is no air blowing, or if the air is not cool, or if there are no openings to the roof ducts, then you & your dealer need to talk.

I may not live in Florida, but I've camped in 90 degree weather and can keep my unit comfortable with the 13500 BTU unit - slides out.

Please answer the above questions. Thanks.
__________________
Bob

'05 Sun Voyager #8351
https://www.much2see.com/index.html
RJ82much is offline   Reply With Quote
Old 08-30-2008, 10:47 PM   #9
Glen
Junior Member
 
Join Date: Aug 2008
Posts: 6
Default gets 70 inside when 69 outside?!

Bob,
Yes, they have checked the air duct passages and I went through them again today. Originaly the said there was something blocked and they fixed that. I and they have run around with ac thermomenters and had them every where. I do have a 20 degree drop or more from intake to exhaust. today I am camping in a no hookup site in Auburn, IN. I had not ran the air because no more than it does it is a waste of gas in the generator. It got up to 85 hear today and I camme back to camper after lunch. I yhought I would check everything again and the camper wasn't to warm, so I started genorator and allready had a roof vent running. After about 1 hr I shut the roof vent and removed intire panel under roof unit. All openings are as open as they made the cutout to duct. the runs do go past vents to wall, but seam blocked at ends to make air come out of vents. We couldn't tellmuch differance with or without center large vent open or closed. After checking every thing we decided to leave for awhile. We had all windows, curtains to cab, roof vents, and blinds shut. We returned about dark and all was still running. About 10:30 pm with thermostat set at 70 degrees the compressor cycled off for a few seconds. I thought finaly something worked. Then I checked out side and it was 69 degrees. Works great doesn't it?
Glen is offline   Reply With Quote
Old 08-30-2008, 11:49 PM   #10
RJ82much
Senior Member
 
Join Date: May 2005
Posts: 572
Default

Glen,

Forgive that I asked questions for items you have already looked at. It sounds like you have covered about everything,,, without luck. I have very little more to add.

One of my AC motors wouldn't start up after a winter storage. Our dealer is also the AC authorized repair shop so, like you, he got my unit for a week When I got it back, the motor had been replaced it with a new one, but also, like you it now seemed inefficient. So, (with fear in my heart) I climbed roofside & removed the AC cover. What a mess the certified, qualified techs left behind. The foam that was supposed to seal inlet/outlet/outside was crumpled, torn loose, misplaced & didn't seal much at all. They had bent the sheet metal so that the joints had come apart & didn't seal anything or contain cool air. Outside air was getting sucked into the chamber & blown into the MH. And, they had thrown all the scrap wire terminals, cutoffs, etc into the chamber to roll around & get stuck in God-knows-what. In summary, I totally redid the job & all is good. That bunch of hacks will never touch my property again.

Perhaps a topside exam under the cover, is in order?

Here's an idea... If you are in Indianna, maybe you should stop at the Napannee GS factory. They have a free campground to owners. The main offices are next door. The reception area is cool & comfortable while you wait for someone to talk with you & agree to have their service or factory people look at your unit. You won't be popular for just "dropping in", but insist that you won't be leaving their campground till your unit works. While you are there, enjoy the pool, golf course, & whatever else you can get out of them. Oh yeah, if the day wears on without results, insist you need to talk with Scott Pullin (VP of operations). You won't be popular with him either, but you will be taken care of.

I think you've suffered long enough.
__________________
Bob

'05 Sun Voyager #8351
https://www.much2see.com/index.html
RJ82much is offline   Reply With Quote
Old 09-02-2008, 09:39 PM   #11
purduepete2
New Member
 
Join Date: Sep 2008
Location: Indianapolis
Posts: 28
Default

Glen,

I have a 2007 BT 5291 with a 15000 BTU AC and gets the unit Ice cold in 90+ weather with all 3 slides out. As Bob said; you've got a problem that needs an RV technician.
purduepete2 is offline   Reply With Quote
Old 09-04-2008, 04:06 PM   #12
Frank Polimeni
Junior Member
 
Join Date: Aug 2008
Location: Vista Ca.
Posts: 4
Default

Hi All, I own a Gulfstream 6340. The past year has been a nightmare. I also had a AC problem. J&L RV in Fontana Ca fixed the problem. Seems GS did not insulate the from cab area entertanment center. It was a 115 degrees in one of the cabinets. GS said my six Show Dogs were the cause of my problem. I asked what is the differance between 6 adults at 150 lbs and my dogs at 40lbs? They didnt have an answer. Next day J&L called and GS OK'd insulating the front cab area and installing a 15000 Ac unit. All is cool now. I will post my nightmares later.



Frank Polimeni
Vista Ca.
__________________
2007 Endura 6340
Frank Polimeni is offline   Reply With Quote
Old 06-13-2009, 08:02 PM   #13
danangie
Junior Member
 
Join Date: Jun 2009
Posts: 3
Default Same problem new 5291

Hi Glen,
I'm having the same issue with my 5291, did you ever get this resolved?

Dan
danangie is offline   Reply With Quote
Old 07-01-2009, 07:56 AM   #14
bottieri
Junior Member
 
Join Date: Jul 2009
Location: Florida
Posts: 18
Default A/C not cooling 5291 model

Briefly:

The problem with this model and the A/C is air flow. The center outlet (the one on the unit at the filter), must be open or the unit freezes up.

Run the fan only for 15 minutes to thaw it out, then set the thermostat to a comfortable setting (72 or so) and open all the vents and turn it to cool. The problem will be solved.

No A/C unit will cool better or faster no matter how low you set the thermostat. Setting the temperature to say, 60 will not cool the coach faster or better to 72 than setting the thermostat at 72 and leaving it alone.
__________________
Joe, Sandy & the Pups (Griffie, Affie & Kate)
Indian Harbour Beach, FL
08 BT Cruiser, 3S, 5291
Radio KF4FM
bottieri is offline   Reply With Quote
Old 07-01-2009, 02:27 PM   #15
john&scotty
Junior Member
 
Join Date: Aug 2008
Posts: 9
Default A/C

My 5291 does stay cool, but if you open the basement doors, you can feel alot of cool air coming out - you could suggest the the service center caulk the seams in the basement area
john&scotty is offline   Reply With Quote
Old 07-01-2009, 04:40 PM   #16
bottieri
Junior Member
 
Join Date: Jul 2009
Location: Florida
Posts: 18
Default

john&scotty

I could be wrong, but I doubt there is anything to be chalked between the compartments and the living area. Those compartments are separate boxes. What you're probably feeling is the cooler air in the compartments actually falling out as warmer air enters. It may be cooler because of the compartment proximity to the floor of the living space, but not actually coming from the living space.

Well... that's my 2 cents worth.
__________________
Joe, Sandy & the Pups (Griffie, Affie & Kate)
Indian Harbour Beach, FL
08 BT Cruiser, 3S, 5291
Radio KF4FM
bottieri is offline   Reply With Quote
Old 07-03-2009, 10:13 AM   #17
bottieri
Junior Member
 
Join Date: Jul 2009
Location: Florida
Posts: 18
Default

Quote:
Originally Posted by Frank Polimeni
Hi All, I own a Gulfstream 6340. The past year has been a nightmare. I also had a AC problem. J&L RV in Fontana Ca fixed the problem. Seems GS did not insulate the from cab area entertanment center.
Frank Polimeni
Vista Ca.
Frank:

How did you determine that the front cab wasn't insulated behind the entertainment cabinets?

What did they do to correct that? I mean: how did they access it and what did they use to insulate the area?

Thanks for the info,
__________________
Joe, Sandy & the Pups (Griffie, Affie & Kate)
Indian Harbour Beach, FL
08 BT Cruiser, 3S, 5291
Radio KF4FM
bottieri is offline   Reply With Quote
Old 07-05-2009, 02:59 AM   #18
purduepete2
New Member
 
Join Date: Sep 2008
Location: Indianapolis
Posts: 28
Default Cab Insulation

Pull the TV out and it will give you access to the cab over behind the entertainment center.
purduepete2 is offline   Reply With Quote
Old 07-10-2009, 06:35 AM   #19
bottieri
Junior Member
 
Join Date: Jul 2009
Location: Florida
Posts: 18
Default A/C not adaquate in model 5291

Re: BT Cruiser 5291

Further to the A/C not cooling problems reported here.

Today I had a chance to investigate the installation and try to determine why maximum airflow is so important in order to keep the unit from icing over the evaporator coil. And, why so little air was coming out of the remote ducts. Here?s what I found:

1. There doesn?t seem to be an internal control to turn off the compressor before it gets cold enough to freeze the coil. If my memory serves me, it?s called a Pitot tube. I couldn?t find one! So that?s probably why the unit needs full airflow to prevent freezing especially when it?s very humid.

2. The air outlet and air intake on the unit aren?t sealed (separated) very well allowing some cold air to recirculate through the evaporator.

3. The duct system was poorly installed in that there is some sheet metal blocking the inlets to the ducts that distribute air fore and aft.

There is also a problem of Styrofoam and metal trash coming out of the ducts.

Here?s what I did to correct the installation problems, and I hope it corrects the cooling ability of the unit although I won?t know until I get on the road.

I highly recommend that you wear gloves while working around the sheet metal and duct inlets and outlets. The metal is brutal on your hands!

You will need some Aluminum heating - A/C duct tape. Not the common Duck-tape! Use only the rather expensive aluminum peel and stick tape. You don?t want tape coming lose in the vents someday plugging them.

? A. I removed the circular vents; wrapped masking tape around my fingers with the sticky side out, and carefully reached in and picked up (on the tape) all the trash at the outlets. This took several tries, but if you don?t get it out you will be sleeping with and walking on metal shards and Styrofoam beads, forever.

? B. While removing the trash from the ends of the ductwork, straighten the foil to smooth the outlets.

? C. Remove the filter/center duct assembly. There?s 6 screws ? two of which are under the round pop-out covers. A small screwdriver tip will pop those out.

? D. Use aluminum tape to seal the openings between the air intake (filter side) and the air outlet. Seal around the wires and the foam tape to the metal housing along the edges. Seal them real good, as there should be no leaks between the two sections.

? E. At the unit, look into the outlet side at the holes in the wood (that would be on both sides); you?ll see metal hanging down blocking some of the outlets. You?ll also feel some rough curled metal from when they cut the openings. I used a long ? square handle? screwdriver. Using the handle end you can get in there and bend the metal back so the opening is fully open (unblocked by any protruding metal). Using small strips of aluminum tape about 5 or 6 inches long, seal those openings so there is a smooth exit from the A/C housing into the duct. Be sure to press the tape into the crevasse fully and securely so it is firmly in place. The exits into the ductwork should be fully open and smooth with no metal blocking or disturbing the airflow. The duct, wood and A/C housing should be like one piece.


After I finished and reassembled everything, I found the volume of air coming out of the remote ducts is much greater now, and with the main outlet closed there is enough air coming out that I feel confident the bedroom will now be cool and the unit won?t freeze up. However, further testing will be required.

I?ll report further when I get on the road and use the unit normally.

Hopefully, this experience will be helpful and I?d sure like to hear from anyone about it.
__________________
Joe, Sandy & the Pups (Griffie, Affie & Kate)
Indian Harbour Beach, FL
08 BT Cruiser, 3S, 5291
Radio KF4FM
bottieri is offline   Reply With Quote
Old 07-12-2009, 08:47 AM   #20
mfa
Senior Member
 
Join Date: Sep 2006
Posts: 305
Default

Great report. Thanks!
mfa is offline   Reply With Quote
Reply

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Similar Threads
Thread Thread Starter Forum Replies Last Post
Selling 5291 BTCruiser phoebewienke Buy / Sell / Trade 0 01-16-2015 09:03 AM
Dex Cool JimBonnie Class A 3 01-28-2014 06:57 PM
For Sale 2007 Class C Gulfstream BT Cruiser Model 5291 jrsocal Class B+ 0 04-21-2013 02:20 PM
heat and cool while driving 72chevy4x4 Class A 4 07-05-2010 09:11 AM
Water runs out of tank filler and vent, model 5291 bottieri Class C 0 07-13-2009 04:49 PM

» Featured Campgrounds

Reviews provided by

Powered by vBadvanced CMPS v3.2.3

All times are GMT -5. The time now is 02:45 PM.


Powered by vBulletin® Version 3.8.9
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
×