Default Onan 7.5kw QD (Quiet Diesel) Generator

We have a Onan 7.5kw QD (Quiet Diesel) generator that has always ran perfectly until today.

We were traveling and it was running great and generating the electric current to run both our air conditions for appox. 45 minutes when all of a sudden it shut down. The light on the button was flashing 3 times in a cycle indicating that it needed service.

I checked the oil and coolant at the next stop and they were okay. I checked the circuit breaker on the generator and it was okay.

I started the genset up again and the engine runs fine, BUT it does not put out and 110 volt current.

I checked all the breakers in the coach and I cannot figure out what is wrong.

Any experts out there or maybe someone has had this problem that could give some clues at what to check??

It is no longer flashing any codes.

Thanks, Ron
GStream40 is offline   Reply With Quote
Old 06-09-2008, 01:33 AM   #2
djqualls
Senior Member
 
Join Date: Aug 2006
Location: Tecumseh
Posts: 175
Default

Ron,

Did you put a meter at the genset?

Have you opened the transfer switch and checked that for voltage?

Did you cycle the main breaker at the Genset?

Only thing I can think of at the moment.

Good Luck.

Dave......
__________________
2006 TourMaster T-36 / Good Sams / FMCA 380624
djqualls is offline   Reply With Quote
Old 06-09-2008, 11:47 AM   #3
RJ82much
Senior Member
 
Join Date: May 2005
Posts: 572
Default

Your generator will shut down when your fuel tank reaches something like 1/4 to 1/3 tank.

There is a likelyhood that the breakers at the generator have tripped if you were using the AC units. Hint for this: turn the thermostat fan control to "manual" so that fan is on all the time. Give it a couple seconds before turning on the AC. The AC will cycle on & off but not the fan. This greatly reduces the current surge that often trips the generator breaker.

Let us know what you discover
__________________
Bob

'05 Sun Voyager #8351
https://www.much2see.com/index.html
RJ82much is offline   Reply With Quote
Old 06-09-2008, 09:57 PM   #4
GStream40
Site Team
 
Join Date: Nov 2005
Posts: 936
Default

Dave,
I checked the main breaker at the genset and cycled it, didn't help.

I have to put a meter at the genset and check it for voltage as soon as the outside temp cools down, it has been around 90 the last couple of days, way too hot for me to be messing around.

RJ,
We have 3/4 tank of fuel. The genset engine runs fine, just no 110 volt.
The breakers on the outside of the unit didn't trip.

Thanks for the hints, will follow up on them.

Ron
GStream40 is offline   Reply With Quote
Old 06-10-2008, 12:29 AM   #5
rdlamb
Senior Member
 
Join Date: Jun 2007
Posts: 386
Default

Ron:
Do you have 1 or 2 breakers on the generator?

Mine has a 37 amp x 2 single breaker. It went out. As explained to me via Cummins/Onan the breaker sends out 2 lines, capable of 37 amps each. When you run 2 A/C(s) you may exceed the 37 amp load of one line as the start up of both A/C(s) draw a lot of amps.

The switch blew one line. The generator would run fine, but no 110 output.
I checked the transfer switch (under your bed), and no 110 in from the generator. Fixing a generator was out of my league, so a service call ensued.

Onan replaced the switch with a "newer" or "improved" switch, and everything seems to be running well.

Always seems to happen when it gets hot outside. Mine went out during the 8 weeks of 100 deg + weather that cooked San Antonio last spring.



__________________
Safe Travels
Rick
07 TM 40D;ISL 450 Cummins(upgraded). Very happy w/coach
Gnarly toad to scoot around.
Geocaching, hiking, fishing, National Parks, Civil War sites.
rdlamb is offline   Reply With Quote
Old 06-11-2008, 07:26 AM   #6
GStream40
Site Team
 
Join Date: Nov 2005
Posts: 936
Default

Well yesterday afternoon I started checking things out.
Started with checking the genset wiring at the junction box that is mounted on the firewall behind the "hood" on the front of the coach.

To my surprise the genset was putting out 122 volts on both legs, well within range.

So I went to the transfer switch that is located under the cedar chest at the foot of the bed. I had 122 volts coming into the switch at the generator teminals, but nothing to the output side of the transfer switch.

The switch is a Iota Engineering Co. model ITS-50R Automatic Transfer Switch. Checked their website and downloaded the wiring and manual for this switch.

Read the information they had listed for the Time Delay Module that is built into the unit and how to flip the switch to test if this part is bad since the LED on the module was not lighting up as it should be. I flipped the switch and started the genset hoping that the Transfer switch would operate as was indicated in the instructions if the module was bad.

Nothing, zero, So the switch must have more serious problems.

I found a website for Solar Sellers and they sell the Iota ITS-50R Auto Transfer Switch for $115.00 plus shipping of $16.00.

So I will call them this morning to see if they have it in stock and can ship it right away.

Maybe I can have it by this weekend and get it installed. We are going to leave on the 21st for a week long Gulf Streamers Back Home Rally and we will need the roof airs while traveling, especially if the temperatures get up to 90 like it has been last weekend.

If after I receive the new one and if I am able to repair the old one, then I will keep it for a spare just in case it is needed.

Thanks to everyone for their guidance and input to my problem, it was much appreciated.

Ron
GStream40 is offline   Reply With Quote
Old 06-11-2008, 08:51 AM   #7
rdlamb
Senior Member
 
Join Date: Jun 2007
Posts: 386
Default

Bravo Ron, and thanks for the detailed recipe on how to test your system when the generator does not provide power to the coach.



__________________
Safe Travels
Rick
07 TM 40D;ISL 450 Cummins(upgraded). Very happy w/coach
Gnarly toad to scoot around.
Geocaching, hiking, fishing, National Parks, Civil War sites.
rdlamb is offline   Reply With Quote
Old 06-11-2008, 12:17 PM   #8
GStream40
Site Team
 
Join Date: Nov 2005
Posts: 936
Default

Quote:
Originally Posted by rdlamb
Bravo Ron, and thanks for the detailed recipe on how to test your system when the generator does not provide power to the coach.
Well actually if I was to do it over again, I would start at the transfer switch to see if there was voltage there. It would save some time of opening the junction box and bearing/retapeing the wiring connections for the tester to make contact with the probes.

Ron
GStream40 is offline   Reply With Quote
Old 06-14-2008, 07:07 PM   #9
GStream40
Site Team
 
Join Date: Nov 2005
Posts: 936
Default

WOW, talk about great and fast service, I order the new transfer switch on Weds. and it was delivered in Friday's mail. Great service by the USPS Priority Mail and John Drake Services http://www.solarseller.com/index.htm

I installed the new transfer switch today and everthing works great, genset power was deliver trough the transfer switch and I ran the both air conditioners for about an hour.

After I was all done, I took the old failed transfer switch apart, checked the coils, contracts, and wiring. All checked okay. Then I removed the Time Delay Circuit board and found a small burnt hole with black around it in the bottom of the circuit board. Hmmmm

Guess I found the failed part. I just ordered a new circuit board from Solar Sellers, John Drake Services for $16.00. I will install it and the test the transfer switch, if all is well then I will have a working spare just in case it is ever needed again.

All is well...

Ron
GStream40 is offline   Reply With Quote
Old 05-22-2018, 08:23 PM   #10
neondon
New Member
 
Join Date: Apr 2018
Posts: 27
Default

Thanks all for the tips for this still-learning "master." I'll check under the bed for the transfer switch power and delay components before I start removing wheels, engines, etc. ...
neondon is offline   Reply With Quote
Reply

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Similar Threads
Thread Thread Starter Forum Replies Last Post
Onan 7.5 DKD Generator Start Switch Track29 Electrical 1 06-17-2019 03:50 PM
Onan Generator problem Wild Irish lad Electrical 4 09-16-2013 03:12 PM
Onan Generator, Gulftream Scenic Cruiser RayHarkness Class A 3 06-19-2013 11:41 AM
8kw Onan Diesel Generator........ stonesfan Electrical 2 12-02-2011 04:22 AM
Defective ONAN generator roada Class A 0 09-15-2010 11:21 PM

» Featured Campgrounds

Reviews provided by

Powered by vBadvanced CMPS v3.2.3

All times are GMT -5. The time now is 12:27 PM.


Powered by vBulletin® Version 3.8.9
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
×